Troubleshooting
Fixing HMI Read Errors to a Servo and PLC on One RS-485 Line
A read error after merging two DOPSoft projects is usually three faults stacked: colliding station numbers, an HMI link using a PLC-only controller driver so servo tags fail to compile, and an RS-485 pair that never reaches CN3. Set the servo to station 1 (P3-00) and the PLC to station 2, select Delta Controller ASCII, then treat a pure timeout as wiring.
How-to
Connecting an HMI directly to a VFD over Modbus RTU
Yes. An HMI with a Modbus RTU master driver can start, stop, set speed and read status and faults from a Modbus-ready VFD with no PLC — after the drive's run-command and frequency-reference parameters point at the serial port, and after communication loss stops the drive in a defined way. Keep the hardwired emergency stop.