HMI and touchscreens
Touch panels and operator terminals: calibration, communication, screen programming and replacement.
Latest articles
How-to
Connecting a Pro-face HMI to a Mitsubishi FX2 PLC
License GP-Pro EX through Pro-face or an authorized distributor, select the Mitsubishi Electric Corporation FX serial driver for the FX2's built-in programming port, build the cable to the documented pinout, and prove the link with one read-only tag before enabling any writes. A connector that fits proves nothing.
How-to
How to Configure WinCC 7.0 PLC Connections With STEP 7
No. WinCC 7.0 and STEP 7 5.4 never connect to each other; each one talks to the PLC, so configure two separate paths: the S7Online access point for STEP 7, and in WinCC Tag Management the MPI channel's Logical device name set to MPI (PLSIM for simulation). Acceptance is one known PLC value displayed live with valid status.
Explainer
How WinCC and STEP 7 Work Together in a PLC Project
STEP 7 configures and programs the Siemens PLC; WinCC builds the operator screens that read and write selected PLC variables over a configured connection. The boundary between the tools is the tag: STEP 7 owns the variable, WinCC owns the display and command objects bound to it.
How-to
Scaling Analog Inputs for Both PID and HMI Display in Ladder
Configure the 1769 analog channel for engineering units X1 across the transmitter span, set the CompactLogix PID scaling to the same range, and display that one tag on the PanelView Plus. Decimal-place settings change appearance only; add a single CPT rate-and-offset rung only when a consumer needs different units.
Selection guide
Pulse Versus 4-20 mA Flow Measurement for a Small PLC Retrofit
Use a pulse-output flow meter into the MicroLogix 1200's built-in high-speed counter for the 180-300 mL batch volumes and compute V = N/K in the PLC; use a 4-20 mA transmitter into a 1762-IF4 only for live flow rate. Continuous tank inventory needs a level measurement, not a fill-line total. The PanelView 300 displays only the value the PLC computes.
Troubleshooting
Why a Call Recipe Object Disappears Inside a Popup Window
The C-more Call Recipe object is not supported inside a popup window: the panel drops it instead of showing it, because it opens its own Recipe Sheet over the display. Move the Call Recipe button to a normal screen and keep parameter entry in the popup, or test the plain Recipe object for loading values in place.
Troubleshooting
Fix Vijeo Designer WebGate not working after an update
Match the WebGate client version on the operator PC to the Vijeo Designer version that performed the last transfer to the panel, then open the session in Microsoft Edge. If it still fails, classify it by stage: unreachable page, client that will not load, authentication, or application without remote functions.
How-to
Showing Tags From Five PLC-5 Processors on One PanelView Plus
Yes. One PanelView Plus screen can show tags from all five PLC-5/25 processors, because each object resolves through its own shortcut to one controller's station address on DH+. Configure five shortcuts and prove one known live value from each processor before building production screens.
How-to
How to Convert a WinCC Project From 1024x768 to 800x600
WinCC has no tool that converts an existing 1024x768 project to 800x600 automatically: you set the smaller picture size, then move and resize objects screen by screen. Because both resolutions are 4:3, the runtime adapt option scales everything uniformly to 78.125% with no distortion - usable as an interim display, but do the manual relayout for a permanent station.
Troubleshooting
What WinCC Error 0180 Means and How to Fix Activation
Error 0180 is the S7DOS code DRIVER_NOT_INST, decimal 384: the driver WinCC tries to start is not installed, has incompatible parameters, or holds an invalid handle. Fix the driver first; 424d after disabling alarm logging and the missing data-server message are downstream results, not separate faults. The project is fixed only when it activates with tag and alarm logging both enabled.
How-to
Using Vijeo Designer 6.2 to program an HMISTU series HMI
HMISTU terminals sit outside the Easy HMI offer that Vijeo Designer Basic programs, and no communication setting adds them. Install regular Vijeo Designer 6.2, take it to the SP12 service pack level, confirm the complete terminal reference appears in the target list, then build and transfer.
Troubleshooting
Why Weintek HMI Tags Fail to Update With an Omron CJ1M
A clean download and system traffic in EasyDiagnoser prove the transfer path, not tag exchange. With a CJ1M-CPU12 and an ETN11, fix the link in order: the documented CJ/CS/CP FINS driver and its destination fields, one known D-word read, then request and reply diagnostics that name which of four stages fails.