HMI and touchscreens
Earlier articles
Troubleshooting
Why Touch JOG Buttons Start Late but Mouse Works Fine
The start delay is Windows press-and-hold recognition holding the touch contact before your button handler fires; mouse clicks skip that path entirely. Bind jog start to touch-down and jog stop to touch-up instead of click or hold events, and the wait — typically near half a second — disappears.
How-to
Why C-more Micro Preview Screens Show Out of Order
Preview thumbnails in C-more Micro follow the project's stored Screen Library list order, not the screen number, and Preview has no sort function. Fix the sequence by dragging entries in the Screen Library; never renumber screens, because every screen-change reference stores the number.
How-to
Connecting a C-More HMI to a Schneider M340 over Modbus TCP
Yes. Select the Modicon Modbus TCP/IP driver in the C-More project, give the M340 a static IP address because its Ethernet modules default to dynamic addressing, and map each %MW word N to the one-based register reference N+1 — the field-documented case reads %MW62200 at 462201. Verify with one known word before building screens.
How-to
Exchanging HMI memory data with a custom PC application
Yes. The panel is the master and the PC program is the endpoint it polls: set the HMI project to Memory Link, then implement that command set, addressing and framing so every read and write the screen sends gets a valid answer. The exact model's communication manual supplies the frame format and memory areas; nothing else should be guessed.
Troubleshooting
Why HMI pages lag with many PLC variable bindings
The lag is acquisition workload, not the processor. On this target each @PLC.variable binding becomes its own Modbus message, so a 140-variable alarm page needs 3.4 to 3.9 s of wire time per full sweep at 9600 baud. Keep direct bindings to roughly 40 values per page for a one-second sweep, and move denser pages to programmed grouped reads into display globals.
Comparison
WinCC Explorer vs Advanced, Professional, Flexible and Unified
WinCC Explorer is only the project shell of WinCC Classic, the pre-TIA Portal PC SCADA system. Advanced and Professional are TIA Portal products — Advanced for panel-style visualization and Runtime Advanced on a PC, Professional for data-heavy PC SCADA — Flexible is Advanced's out-of-date predecessor, and Unified is the web-based generation on Linux-based panels. For a new S7-1200 SCADA, engineer it in TIA Portal as WinCC Professional or Unified; the S7-300 SIMATIC Manager plus Explorer path does not carry over.
Troubleshooting
Fixing unsupported device errors when downloading an MER file
The unsupported device warning at MER creation is a compatibility fault, not a network fault: in the reported case a V32 controller with a V10 terminal was cleared by upgrading the terminal to V11. Then aim ME Transfer Utility at the HMI node, not the PLC, and keep the .mer in the standard Runtime folder.
Troubleshooting
Upload a PanelView 600 Program When DF1 AutoConfigure Fails
When RSLinx AutoConfigure fails on a PanelView 600, configure the DF1 driver manually at the terminal's power-up defaults - 9600 baud, CRC error checking, no parity, 8 data bits, 1 stop bit, no handshaking - then upload with PanelBuilder32. The unreadable display does not block serial recovery, and the memory card is not a guaranteed source copy.
Troubleshooting
Why FactoryTalk View SE Clients Wireframe While Servers Show Active
Wireframed FactoryTalk View SE clients with servers showing Active mean live data cannot be acquired from the data providers, and an Active server state never proves that path. Prove the path in a blank local SE project with one FactoryTalk Linx server and one shortcut, then rebuild the converted application in tested increments; the reported recovery came only from a ground-up rebuild with imported graphics and manual shortcuts.
Troubleshooting
Why HMI Screens Fill With Question Marks After a Return Goto
Question marks filling a screen after a return Goto mean the display's objects cannot resolve their tag values. The usual cause after adding a return button is a parameterized display opened without its parameters. Compare the failing route with a known-good route to the same display before touching communications.
How-to
Showing a PLC Connection Fault on a Comfort Panel Alarm Display
Enable the Comfort Panel's connection and disconnection system alarms, add an alarm buffer view, and drive a persistent HMI-local status tag from their events, because the system message shows for about 2 seconds and then leaves the screen while values freeze; a PLC clock heartbeat adds a stale-data check.
How-to
How to Add an XY Plot to a WinCC Application
No. Classic WinCC's base graphics objects stop at the bar graph and the time trend, so a value-against-value plot comes from a third-party ActiveX/OCX control, verified against your WinCC edition and licensed for engineering and runtime separately. Map the 20-element array first: 20 Y values, 10 X/Y pairs and 20 points need different point and series capacities.